680.24 Junction Boxes and Electrical Enclosures for Transformers
or Ground-Fault Circuit Interrupters.
(A) Junction Boxes. A junction box connected to a conduit
that extends directly to a forming shell or mounting bracket of
a no-niche luminaire shall meet the requirements of this
section.
(1) Construction. The junction box shall be listed, labeled,
and identified as a swimming pool junction box and shall
comply with the following conditions:
(1) Be equipped with threaded entries or hubs or a nonmetallic
hub
(2) Be comprised of copper, brass, suitable plastic, or other
approved corrosion-resistant material
(3) Be provided with electrical continuity between every
connected metal conduit and the grounding terminals by
means of copper, brass, or other approved corrosionresistant
metal that is integral with the box
(2) Installation. Where the luminaire operates over the low
voltage contact limit, the junction box location shall comply
with (A)(2)(a) and (A)(2)(b). Where the luminaire operates at
the low voltage contact limit or less, the junction box location
shall be permitted to comply with (A)(2)(c).
(a) Vertical Spacing. The junction box shall be located
not less than 100 mm (4 in.), measured from the inside of the
bottom of the box, above the ground level, or pool deck, or not
less than 200 mm (8 in.) above the maximum pool water level,
whichever provides the greater elevation.
(b) Horizontal Spacing. The junction box shall be located
not less than 1.2 m (4 ft) from the inside wall of the pool,
unless separated from the pool by a solid fence, wall, or other
permanent barrier.
(c) Flush Deck Box. If used on a lighting system operating
at the low voltage contact limit or less, a flush deck box shall be
permitted if both of the following conditions are met:
(1) An approved potting compound is used to fill the box to
prevent the entrance of moisture.
(2) The flush deck box is located not less than 1.2 m (4 ft)
from the inside wall of the pool.