The problem was that a emt conduit in a bank building had become energized due to a ground fault in the light fixture that it fed. The conduit had become separated, eliminating the only grounding path to the panel, and killed an electrician.I determined that the (bank) building had been built prior to the NEC requirement that a continuous grounding wire be carried through the conduit. Subsequent versions didn't permit conduit to be used as the ground path.
I remember something about that from when I lived in Chicago. Local codes, such as the Chicago Electrical Code (I think that is what it is called), can be more restrictive than the NEC. But the article seems to be saying that the NEC itself has eliminated the use of conduit as an EGC. That is not true, as Don has already said.Originally posted by scott moran: I am from the metro Chicago area and the only installations allowed is with EMT.
Are you sure? I was thinking this could have been a jail or prison, and one of the "residents" sealed the box.Originally posted by augie47: