That A 3-point Saddle Of Any Degree Counts For 180 Degrees Of A Conduit Run. Please Confirm.
jrannis said:Im seeing 90 deg max. Look for a place to put a "C" condulet if you are over just a bit
360 is the answer.Matters not how or direction.Often this rule is bit overkill on short runs but an inspector can force it and it does include box offsets.76nemo said:How do you make your saddles is the true question at hand. I am a maintenance guy, from what little I know, it's 360 max.. Am I wrong?
76nemo said:I am a maintenance guy, from what little I know, it's 360 max.. Am I wrong?
raider1 said:Take a look at 385.26 for the the number of bends allowed in EMT conduit.
Chris
infinity said:What do you mean by 90 degrees max? Would a 30-60-30 offset be a violation?
Dennis Alwon said:That's 358.26 not 385.26
jrannis said:That was a comment to the 22.5 /45 /22.5 answer.
I think the NEC used to mention the max was "four quarter bends". I cant see a reasonable inspector turning someone down for an extra small kick or box offset.