masterinbama

Senior Member
As long as the cubic inches are permanently marked on the conduit body. Had an inspector burn me on that one once. PVC LB no markings but the guy is a notorious nitpicker.
 

realolman

Senior Member
In order to splice 2 #16 awg to 2 #14 awg, you'd need at least a 3/4" LB,LR,T, or C. http://www.appletonelec.com/PDF/AEC%20FM9.pdf

I see it all the time, too.... Half inch LB, or maybe a T with several #14 wires continuing on through with two of them spliced to a solenoid coil.

Actually in many cases , there does seem to be plenty of room, though.

A 1/2" C or LB with 2 - 14's spliced to 2 - #16's is gonna look half empty...

or is it half full?...

I'd like to be an optimist, but I just don't think it'd work out.:wink:
 

luckyshadow

Senior Member
Location
Maryland
Besides splices in an unmarked LB I have a problem with Electricians that over fill a LB.
Just last week I had a contractor that had a 3" LB with 4 350 KCMIL conductors in it.
Stamped in the LB was: Max no. conductors :3 - 4/0 .
 