Does not 370-15(a) prohibit one from installing regular old steel conduit boxes Steel City #52141 and flat blank covers outdoors? I can't beleive that these boxes are "listed for wet locations".
I have seen way too many installations on the sides of buildings and attached to the tops of parapet walls for exerior lighting where these boxes were used with EMT and I just need to be sure here. I had some guys argue that they were in compliance because the boxes had holes in them therefore they provided drainage.
Wouldn't one need to use something like a cast aluminum "Bell" box, raintight gland-type fittings and THW or equal conductors?
I have seen way too many installations on the sides of buildings and attached to the tops of parapet walls for exerior lighting where these boxes were used with EMT and I just need to be sure here. I had some guys argue that they were in compliance because the boxes had holes in them therefore they provided drainage.
Wouldn't one need to use something like a cast aluminum "Bell" box, raintight gland-type fittings and THW or equal conductors?