Conduit cast in place = firestopped?

Status
Not open for further replies.

Natfuelbilll

Senior Member
Is a RGS conduit installed and then a concrete wall poured around it making it cast in place complete with regard to 2 hr fire stop?

Or must I install a fire stopping split sleeve around the conduit and then pour the wall?
 
No firestop is required. A smear of firestop around a conduit encased in concrete will do absolutely zero (I have seen guys do it anyway to satisfy a brainless inspector).
 