I was in my training class the other night and we are covering conduit bending. The subject came up as to how many bends the NEC allows in one run of conduit. My instructor was talking about a "100 foot rule" in the NEC that limits the amount of bends to 360 degrees in a 100ft run of conduit, he didn't tell us where in the NEC to find the rule, he just told us to look it up. So I did. I like to think I am a damn good apprentice and will make a damn good electrician one day but I couldn't find the "100ft rule". This is what I found:
342.26
344.26
358.26
All these articles state the same thing:
"There shall not be more than the equivalent of four quarter bends ( 360 degrees total ) between pull points, for example, conduit bodies and boxes."
This statement is even true for the Nonmetallic and flexible conduit. So conforming this 100ft rule to real life is that if I have 100ft of conduit between two J-boxes then I can't have more then 360 degrees of bends between the two J-boxes. That seems like an awfully long length of conduit between the J-boxes. I was expecting a shorter run I guess. The NEC doesn't limit the number of J-boxes but I don't want an ugly installation either. I still have allot to learn. Is this 100ft rule a personal preference or is it really in the NEC somewhere?
Thanks for your help,
Kevin
342.26
344.26
358.26
All these articles state the same thing:
"There shall not be more than the equivalent of four quarter bends ( 360 degrees total ) between pull points, for example, conduit bodies and boxes."
This statement is even true for the Nonmetallic and flexible conduit. So conforming this 100ft rule to real life is that if I have 100ft of conduit between two J-boxes then I can't have more then 360 degrees of bends between the two J-boxes. That seems like an awfully long length of conduit between the J-boxes. I was expecting a shorter run I guess. The NEC doesn't limit the number of J-boxes but I don't want an ugly installation either. I still have allot to learn. Is this 100ft rule a personal preference or is it really in the NEC somewhere?
Thanks for your help,
Kevin