William K Hicks
New member
I am just looking for some other opinions as far as when coming into a pull box on the outside of a building and through the wall into a switchboad. The conduits come up into the bottom of the box and leave the back of the box. Code staes that the distance between raceways for angle pulls needs to be 6 times the trade size of the conduit. Although the exception states that if a raceway enters in a wall of the box where there is a removable cover then the distance from the entry to the cover can be determined by using table 312.6A. My question is does the exception alow you to not have to use the 6 times the trade size of the conduit between raceways. We have a limitted distance as far as entry into the back of the switchgear and may not be able to get to 6 time the trade size. Is this exception just for use in determining the depth of the box for this type pull or is it intended for the proper wire bending radius?