Conduit Fil
TWGJ24
Say we have a 3/4 PVC Sch. 40 Conduit 100 feet long. How many number 12 Thhn wires can I put in this conduit if I am using diveristy and each circuit is non continuous load of 1200w. I am figuring that I can put in 12 Current carrying conductors. IF I am wrong please explain why and how you come up with something else.
Thanks
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
Two things you must do. Figure how many conductors will fit in the conduit then determine the number of ccc and derate. This question cannot be answered because we don't know if the load is 120V on a single phase or three phase system. We also don't know if the load is 120 or 240. I would assume 120V.
infinity
New Jersey
Journeyman Electrician
What table are you using for your diversity calculations? If you use the standard derating table {TABLE 310.15(B)(3)(a)} your 12 CCC's would require an adjusted ampacity of 50% which equals 15 amps. (30 * 50% = 15) For a 1200 watt load your good on a 15 amp OCPD.
Dennis Alwon
Chapel Hill, NC
Actually I think it will work out the same for single phase or 3 phase but I think 12 is not correct. You say 12 CCC but the question is how many conductors.
infinity
New Jersey
You can fit 15-#12 THHN conductors in a Sch-40 PVC. He said 12 CCC's so that's possibly 6-120 volt circuits.
david luchini
Connecticut
Engineer
Yup, that would work if all of the circuits could operate on 15 amp OCPD's.
Yes, and with 15 OCPD's, we could put twenty (20) #14 THHN CCCs and one EGC in the 3/4" PVC to handle the 1200W loads...assuming the loads are not multiple receptacle outlets for cord-and-plug connected portable loads.
infinity
New Jersey
Yes, unless the PVC is longer than 24". ;)
dana1028
Load Diversity
Load Diversity
I'm wondering if the OPs actual question is about using 'diversity' to determine the number of conductors without having to use T310.15(B)(15) to derate.
There is an example in the 2008 in Annex B [B310.11] using the 'diversity allowance' to calc the diversity and thus not have to derate sometimes. I haven't actually used these calcs but have seen this example in the NEC.