Hi all.
I have a 4" PVC Sch 40 in my design. This conduit run, with a few ground boxes, is approximately 600 feet before conductors go their separate ways.
In the 4" PVC, I am powering roadway equipment using a 120/240 service. Inside the 4" PVC, I have 18 conductors (mix of xhhw, neutral, and grounding). The area for all wires is about 3.75 square inches, which is about a 30% fill.
I know the NEC allows up to a 40% fill for 3+ conductors, but should I be looking to use a second conduit to make things easier on construction?