H High Peak Member Feb 25, 2009 #1 On a 20 amp circuit on a dimmer panel, how many number 10 thnn current carrying conductors are allowed in a 1" EMT conduit without derating? How many equipment grounding conductors do you need in the same conduit and what size?
On a 20 amp circuit on a dimmer panel, how many number 10 thnn current carrying conductors are allowed in a 1" EMT conduit without derating? How many equipment grounding conductors do you need in the same conduit and what size?
480sparky Senior Member Location Iowegia Feb 25, 2009 #2 Sounds like a homework question. What answers did you come up with?
raider1 Senior Member Staff member Location Logan, Utah Feb 25, 2009 #3 On a 20 amp circuit on a dimmer panel, how many number 10 thnn current carrying conductors are allowed in a 1" EMT conduit without derating? Click to expand... 3, take a look at 310.15(B)(2)(a). Or are you asking how many #10 can be installed in a 1" conduit before the derated ampacity is below 20 amps? How many equipment grounding conductors do you need in the same conduit and what size? Click to expand... Take a look at 250.122(B) and (C). Chris
On a 20 amp circuit on a dimmer panel, how many number 10 thnn current carrying conductors are allowed in a 1" EMT conduit without derating? Click to expand... 3, take a look at 310.15(B)(2)(a). Or are you asking how many #10 can be installed in a 1" conduit before the derated ampacity is below 20 amps? How many equipment grounding conductors do you need in the same conduit and what size? Click to expand... Take a look at 250.122(B) and (C). Chris