If I am given the diamater for a 3/c #10 and 3/c #2 multiconductor cable do I then take the radius of each of these given diamaters and use pi*r^2 to find the area of each of these cables. Can I then add these two areas and compare this calculated total against the values given in Chapter 9 Table 4 for conduit fill %?
If two cable diameters are. .47" and 1.015" then the radius for these are .235" and .5075". The two areas respectively for these two cables are then .173"in sqrd and .809"in sqrd. Adding these two areas together it comes out to be .982 in_sqrd.
Now if I take this area of .982 and compare it to the Article 344 section of table 4 in chapter 9 for 2" conduit I see that the 40% fill for 2" is 1.363" sqrd. So since my calculated area of .982 is less then the 40% value of 1.363" then it is o.k to pull these cables in this 2" size conduit?
Anybody see any problems with my calculations?