Will Wire
Senior Member
- Location
- California: NEC 2020
- Occupation
- Electrical Contractor
I recently did a conduit fill calculation for three # 4 THHN, and one # 6 THHN and arrived at 0.2979 cubic inch. According to Chapter 9 tables it will fit in 1" EMT. The 1" LB states maximum fill is three # 4 conductors. NEC 314.28 (A)(3) says I can't exceed the fill of the conduit body if marked. Is my only solution to up size the conduit run, or bush down a larger LB.
Thanks,
Trent