mdshunk said:
Nothing in that exception applies to you, since you're not entering the top of the enclosure. Plain and simple. To enter the bottom with a cables in a raceway, you need a transition fitting (some call it a combination coupling) or a box. No way around it.

Ah, that could be the missing piece in my description.

Thanks!
 
When I was jerking romex years ago,my boss would have us stub up a 2" pvc out of the panel and into the the attic for our hr's and future use.I guess this was a violation.oops.
 