What is the the max amount of no# 2 copper thwn-2 wires I can get in a 1 inch flex metal conduit ? I see 3 total can I run the ground on the out side of the flex which would be a number 8 thwn-2 and if so can it be bare copper wire .
FYI,With an increase of phase conductor size to a # 2awg, the increased EGC size would be a # 6 awg. Should still fit in the 60% fill x 24" nipple.