Yes I can. My point is that your initial post:
While technically correct could lead to an incorrect answer to the question Fred posed if one did not also consider ampacity adjustments. That they do not come into play here does not mean they can be ignored. If the thread title was "Question?" instead of "conduit fill", would that help you see my point?
Take the exact same question Fred asked, make it this:
"How many #10 THHN wires allowed in 1 inch emt after derating for 30 amp circuits all separate neutrals"
Is that question answerable? and is the answer different than for 20A? yes and yes.
Fill very much has something to do with ampacity because if you put 12 #10 CCC in a 1" EMT conduit on 30A breakers you are going to fail your inspection.
My initial response was called a hint because I already knew the answer and the derating didn't alter the result from the information given. If the raceway were larger you could install more #10 THHN conductors and still be at 20 amps after derating but that's not relevant because of the maximum fill permitted by the NEC for the given 1" EMT.