Setting up a 6a 3 phase sub panel. Running 4awg. I am seeing that I can run 4 pcs of 4awg thhn in 1 inch emt. Now to add the ground will adding 1 pc of 10 awg put be over the limit to where I have to go up to 1-1/4 or would I make it with the 1". thx
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I agree with Rob, after you do it post your results and how you got to your conclusion.

Roger
 

markebenson

Senior Member
Location
fl
I agree with Rob, after you do it post your results and how you got to your conclusion.

Roger

4 pc thhn 4awg, 1pc thhn 10awg / 1" Emt

Total wire area (mm2): 226.25(0.35 in2)

Conduit area (mm2):
556.00 (0.86 in2)

Conduit fill (%): 40.69%

Thanks
 

lordofthisworld

Senior Member
Location
Massachusetts
4 pc thhn 4awg, 1pc thhn 10awg / 1" Emt

Total wire area (mm2):226.25(0.35 in2)

Conduit area (mm2):
556.00 (0.86 in2)

Conduit fill (%): 40.69%
Thanks
ch9 T5
total wire area #4AWG= .0824(in2) x 4=.3296 .3296 + .0211=.3507
total wire area #10AWG= .0211 x 1=.0211

CH 9 T4
over 2 wires 40% (in2) 1” = 0.346 to small
1 1/4” = .598 is the one u want
 

Adamjamma

Senior Member
4 pc thhn 4awg, 1pc thhn 10awg / 1" Emt

Total wire area (mm2):226.25(0.35 in2)

Conduit area (mm2):
556.00 (0.86 in2)

Conduit fill (%): 40.69%
Thanks
But over two wires only allowed forty percent fill... scuse me, live conductors...

but if you used the emt as your ground conductor think you could do it..just no 10 wire... that took you over the size.
 

Adamjamma

Senior Member
Let's wait until the OP posts his numbers.
Ok.., I was right, I think, just did it slightly different but still.. pulled the 40 percent fill for the emt from the one table, then calculated the wire sizes, then checked to see what the next size showed when wire was too big for his first size.

but, am I right that using EMT one can drop the grounding wire, the number ten in his case, and be fine? Mostly work with pvc so always need my grounds, but..
 