Maximum number of #14 THHN in EMT @ 40% fill? Looking for NEC section, I can't locate. Weird I always have bookmarked.
Those tables are based on 53%, 31% or 40% fill...depending on how many conductors can fit in the raceway.Ant those table are based on 40% fill?
40% would be for more than 2 conductors in the raceway.Ant those table are based on 40% fill?
Wait, really? Where the table says "2" that should mean that the fill is no more than 31% with 2 conductors. And where the table says "-" that should mean that one conductor is bigger than 53% of the cross sectional area. Did they really use 40% in all cases?The actual rule is in Chapter 9, Table 1, and the numbers found in Annex C are calculations that have been done for you based on Chapter 9, Tables, 1, 4 & 5. The numbers in Annex C are all based on more than two conductors of the same size in a raceway.
Don, then why would the tables include one and two conductors?The numbers in Annex C are all based on more than two conductors of the same size in a raceway
good pointDon, then why would the tables include one and two conductors?
I like the calculator. So you can get 19 #10's in a 1-1/4" raceway at 40% fill? And would still be good for 20A.This conduit-fill calculator shows calculated fill percentages:
http://www.electrician2.com/rveltrain05/rf_calculator.html
For EMT you can get 28-#10's in 1.25 tubing.I like the calculator. So you can get 19 #10's in a 1-1/4" raceway at 40% fill? And would still be good for 20A.
For EMT you can get 28-#10's in 1.25 tubing.
But they would not be good for 20A as per 310/15(C)(1) they would be rated for 45% of 35A???For EMT you can get 28-#10's in 1.25 tubing.
Here's another one:This conduit-fill calculator shows calculated fill percentages:
http://www.electrician2.com/rveltrain05/rf_calculator.html
40A * 45% = 18ABut they would not be good for 20A as per 310/15(C)(1) they would be rated for 45% of 35A???
Now that’s impressive..Not big on these things they call “apps” I just got a “smart phone” about a year ago, but…..
This is I think the only “app“ I have. It’s great for quick ampacity and conduit fill calculations.
View attachment 2560201
How do you ask it to calculate minimum conduit size for a given set of conductors (without trial-and-error)?Here's another one: