Augie 47.......314.16(C) (1) mentions the "twice" rule if making splices therein the conduit body. And size 6 AWG is the largest conductor that may be permitted for that reason, larger size conductors installed in a conduit body must adhere to the cubic inch volume as set forth by the MFG, or if no cubic inch volume is noted then the conduit body should be same size as the raceway.
My opinion is that I would not try to make a splice with any size conductor other than a 6 AWG; which would be a size 4 AWG.
Section 314.28 Pull and Junction Boxes and Conduit Bodies. Here we find wire sizes to be 4 AWG or larger. And specific rules for them such as straight pulls, Sect. 314.28 (A) (1) and (2) for angle pulls or u-pulls.
This is where raceways are used and not conductor sizing to determine the size of the conduit bodies used as pull or junction boxes. This is somewhat time consuming and requires more time to arrive at the correct size of the pull box based on raceway sizes and not conductor sizes.
When sizing conduit bodies think of them as if they were raceways. Same rules apply when sizing raceways based on approximate area square inch per conductor as found in Chapter 9, Tables 5. So, you could use a smaller conduit (raceway) but the conduit body must be sized "twice" the cross section area of the largest conduit or, larger than the raceway. In which case you would use reducing fittings installed inside the conduit body.
You will be applying Chapter 9 and Table 5 and Table 314.16 (B) (1).Conductors allowed in a conduit body and conductors allowed in a raceway when determing square inch per wire size and a table from Chapter 9 for various raceways.