T Tom L. New member Feb 14, 2007 #1 If I am installing multiple power limited multi conductor cables, do I still need to use 40% fill requirements from Chapter 9 table 1 (9)?
If I am installing multiple power limited multi conductor cables, do I still need to use 40% fill requirements from Chapter 9 table 1 (9)?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Feb 14, 2007 #2 For article 725 class 1, 2 or 3, yes.