Don S. said:
Chapter 9 tables seem to be obsessed with limiting conduit fill to 40% for 3 or more wires. The concerns being potential damage during installation, and heat generation from current flow. Is there a provision any place else in the NEC allowing greater fill for control wires. Modern insulation is so tough that the prospect of damage during installation has been greatly reduced, and there is no heat generated by conductors energized only momentarily.
Found this is the 2008 NEC Handbook. Thought it might be intersting
under 725.1
General Discussion of Remote-Control, Signaling, and Power-Limited Circuits
The wiring methods required by Chapters 1 through 4 of the Code apply to remote-control, signaling, and power-limited circuits, except as amended by Article 725 for specified conditions.
A remote-control, signaling, or power-limited circuit is the portion of the wiring system between the load side of the overcurrent device or the power-limited supply and all connected equipment. The circuit is categorized as Class 1, Class 2, or Class 3.
Class 1 circuits are not permitted to exceed 600 volts. In many cases, Class 1 circuits are extensions of power systems and are subject to the requirements of the power systems, except under the following conditions:
1. Conductors size 16 AWG and 18 AWG may be used if properly protected against overcurrent (see 725.43).
2. Where damage to the circuit would introduce a hazard, the circuit must be mechanically protected by a suitable means. [See 725.31(B).]
3.
The adjustment factors of 310.15(B)(2) apply only if such conductors carry a continuous load. (See 725.51 for the exact requirements for adjustment factors affecting ampacity.)
Class 1 remote-control circuits are commonly used to operate motor controllers in conjunction with moving equipment or mechanical processes, elevators, conveyors, and other such equipment. Class 1 remote-control circuits may also be used as shunt trip circuits for circuit breakers. Class 1 signaling circuits often operate at 120 volts but are not limited to this value.
Conductors and equipment on the supply side of overcurrent protection, transformers, or current-limiting devices of Class 2 and Class 3 circuits must be installed according to the applicable requirements of Chapter 3. Load-side conductors and equipment must comply with Article 725. Class 2 and Class 3 conductors are required to be separated from and not occupy the same raceways, cable trays, cables, or enclosures as electric light, power, and Class 1 conductors, except as noted in 725.136.
Dry-cell batteries are considered Class 2 power supplies, provided the voltage is 30 volts or less and the capacity is equal to or less than that available from series-connected No. 6 carbon-zinc cells. (A No. 6 dry-cell battery is cylindrically shaped with nominal dimensions of 21/2 in. in diameter by 6 in. tall and weighs just over 2 lb. A No. 6 dry-cell battery is about 10 times the volume of the standard D-cell battery commonly used in flashlights.)
Circuits originating from thermocouples are categorized Class 2 circuits. Neither dry-cell batteries nor thermocouples are required to be listed.