Re: Conduit fill
Do you have a ground wire in the nipple?
If so you need to calculate the cross sectional area.
(3) Equipment grounding or bonding conductors, where installed,
shall be included when calculating conduit or
tubing fill. The actual dimensions of the equipment
grounding or bonding conductor (insulated or bare)
shall be used in the calculation.