The Chapter 9 tables are part of the code. The tables in Annex C are not.The chapter 9 tables are for informational purposes and not part of the NEC. Your calcuation is what counts. I've read that the tables even have some errors.
The notes to Table 1 in Chapter 9 strongly imply that you have to use the information in the Chapter 9 tables for your conduit fill calculations. Note 5 says if the conductor is not listed in a Chapter 9 table, then you can use the actual dimensions.
The NEC tables are conservative and in some cases I can fit more cables within a 40% fill.
That could be a listing issue. I think that the standards that the conduits are listed to, specify the wall thickness.It's actually the conduits that appear to have more cross sectional areas than NEC: Galvanized rigid steel, PVC, etc.