Conduit for Input and Output wires

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
Good morning experts,

I am designing a Solar Voltaic System with Enphase equipment from my garage to connect my solar input to the 200A Main Service Panel (MSP) which is 25 feet away.

I have a 60A sub panel in the garage fed by an underground 1” conduit and a double pole 70A breaker from the MSP. If I have all my solar panels install near the garage, I would have my Combiner Box there and have the AC disconnect near/next to the MSP.

Since I cannot run another underground conduit between my garage and the MSP because the surface is paved. I would like to use the existing feeder to my garage to connect my solar input from the combiner Box to the MSP via the AC Disconnect. By doing that, I lost my utility supply source to the garage.

As I only need to feed my MSP with 40A (#8 wires) from the solar source (Combiner Box), and in order to maintain/keep the utility supply source to my garage, I would like to replace/downsize the feeder with #8 wires (40A). That means my underground feeder conduit will have input and output 7 #8 wires (reduced one Ground wire ). Also I need to add 4 #18 wires for Consumption CTs , the total conduit fill is still under 40%.

Just wonder whether it is ok per NEC to run the input and output wires in the same conduit? Also it is hard to put all the wires through the 1" underground conduit - the only bend is the two ends where they daylight? I will check with my electrician, just want to make sure it is workable.
 

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
Why can't you backfeed the garage sub?
I have a 1" 70A feeder but adding a grid-tie solar requires another underground conduit/wires which is not possible. Downgrade the 70A to 40A so that I could use 7 #6 + 4 #18 wires is viable, pulling those wires through is tough , may not be possible.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I have a 1" 70A feeder but adding a grid-tie solar requires another underground conduit/wires which is not possible. Downgrade the 70A to 40A so that I could use 7 #6 + 4 #18 wires is viable, pulling those wires through is tough , may not be possible.
You didn't answer the question. Why can't you backfeed the subpanel?

There is no code reason you can't put your solar breaker in the garage subpanel. Is there a utility requirement that's a problem?
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
You didn't answer the question. Why can't you backfeed the subpanel?

There is no code reason you can't put your solar breaker in the garage subpanel. Is there a utility requirement that's a problem?
You can't put a 40A backfed solar breaker in a 60A-rated subpanel - 705.12(B). You can tap the feeder though in the subpanel if the 70A breaker in the Main loadcenter is moved to the bottom position/opposite main breaker. But still have to resolve the CT extension wire issue.
 
Last edited:

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
You can't put a 40A backfed solar breaker in a 60A-rated subpanel - 705.12(B). You can tap the feeder though in the subpanel if the 70A breaker in the Main loadcenter is moved to the bottom position/opposite main breaker. But still have to resolve the CT extension wire issue.
Sorry, I missed those details.
I imagine the 60A panel could be replaced with a 125 more easily than doing a new conduit and/or wire. What's that doing on a 70A breaker anyway?

CT extension is another issue, but then I wonder if that's really necessary.
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
Good morning experts,

I am designing a Solar Voltaic System with Enphase equipment from my garage to connect my solar input to the 200A Main Service Panel (MSP) which is 25 feet away.

I have a 60A sub panel in the garage fed by an underground 1” conduit and a double pole 70A breaker from the MSP. If I have all my solar panels install near the garage, I would have my Combiner Box there and have the AC disconnect near/next to the MSP.

Since I cannot run another underground conduit between my garage and the MSP because the surface is paved. I would like to use the existing feeder to my garage to connect my solar input from the combiner Box to the MSP via the AC Disconnect. By doing that, I lost my utility supply source to the garage.

As I only need to feed my MSP with 40A (#8 wires) from the solar source (Combiner Box), and in order to maintain/keep the utility supply source to my garage, I would like to replace/downsize the feeder with #8 wires (40A). That means my underground feeder conduit will have input and output 7 #8 wires (reduced one Ground wire ). Also I need to add 4 #18 wires for Consumption CTs , the total conduit fill is still under 40%.

Just wonder whether it is ok per NEC to run the input and output wires in the same conduit? Also it is hard to put all the wires through the 1" underground conduit - the only bend is the two ends where they daylight? I will check with my electrician, just want to make sure it is workable
Good morning experts,

I am designing a Solar Voltaic System with Enphase equipment from my garage to connect my solar input to the 200A Main Service Panel (MSP) which is 25 feet away.

I have a 60A sub panel in the garage fed by an underground 1” conduit and a double pole 70A breaker from the MSP. If I have all my solar panels install near the garage, I would have my Combiner Box there and have the AC disconnect near/next to the MSP.

Since I cannot run another underground conduit between my garage and the MSP because the surface is paved. I would like to use the existing feeder to my garage to connect my solar input from the combiner Box to the MSP via the AC Disconnect. By doing that, I lost my utility supply source to the garage.

As I only need to feed my MSP with 40A (#8 wires) from the solar source (Combiner Box), and in order to maintain/keep the utility supply source to my garage, I would like to replace/downsize the feeder with #8 wires (40A). That means my underground feeder conduit will have input and output 7 #8 wires (reduced one Ground wire ). Also I need to add 4 #18 wires for Consumption CTs , the total conduit fill is still under 40%.

Just wonder whether it is ok per NEC to run the input and output wires in the same conduit? Also it is hard to put all the wires through the 1" underground conduit - the only bend is the two ends where they daylight? I will check with my electrician, just want to make sure it is workable.
Are you thinking about an EV charger in the near future? If there is another path to get from the MSP in house to the garage, like trenching around the pavement, I would think about future needs before you do anything. A 60A sub in the garage is not sufficient if EV in your future. Coupled with the other challenges you have with the PV arrangement you describe, it might be best to just trench around and install 1.5-in or 2-inch conduit for an upgraded feeder to garage subpanel, and the solar inverter/combiner output back to MSP, along with a 1-inch conduit for CT wiring + an extra cat6, and another 1-inch conduit for future/spare. You could either backfeed the subpanel right in the garage with the solar or run it back to the main in the house. You can size everything as needed and solve all your issues this way. Also, if you are running CT extension wires, they really need to be in twisted, shielded cable while they run with any power powers in conduit, you can't just run #18 THHN with power wires and expect it will work.
 

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
Thanks you solarken.

As you said going around and thinking about future upgrade make more sense to me now.
Initially, I am just trying to be cheap . Going around for me only add additional 30 feet of wires and that isn't bad at all. Yes, I would go for that option and also since I just have to trenching once, I would add 1" conduit for the CT wires with CAT 6 wires go with it.
 

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
Sorry, I missed those details.
I imagine the 60A panel could be replaced with a 125 more easily than doing a new conduit and/or wire. What's that doing on a 70A breaker anyway?

CT extension is another issue, but then I wonder if that's really necessary.
Thank you for reviewing and participating. Solarken has nailed and gave me the solution.
 

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
Thanks solarken for sharing your expertise.
As I am planning to use Enphase IQ8+ and combiner 4 and Solar only for now. I plan eventually to add the System Controller 2 and IQ Battery as upgrade. As my solar panels are at the garage area, 25 feet apart and away from the Main Service Panel. Need to put underground conduits as suggested. The Combiner Box 4 would definitely be placed near the garage area. Where should the System Controller 2, and IQ 8 battery be placed best? Near MSP or near the garage?
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
Thanks solarken for sharing your expertise.
As I am planning to use Enphase IQ8+ and combiner 4 and Solar only for now. I plan eventually to add the System Controller 2 and IQ Battery as upgrade. As my solar panels are at the garage area, 25 feet apart and away from the Main Service Panel. Need to put underground conduits as suggested. The Combiner Box 4 would definitely be placed near the garage area. Where should the System Controller 2, and IQ 8 battery be placed best? Near MSP or near the garage?
Sorry, I am not up to speed on Enphase energy storage or their controller.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Thanks solarken for sharing your expertise.
As I am planning to use Enphase IQ8+ and combiner 4 and Solar only for now. I plan eventually to add the System Controller 2 and IQ Battery as upgrade. As my solar panels are at the garage area, 25 feet apart and away from the Main Service Panel. Need to put underground conduits as suggested. The Combiner Box 4 would definitely be placed near the garage area. Where should the System Controller 2, and IQ 8 battery be placed best? Near MSP or near the garage?
The System Controller should go near where you want your backup subpanel, which I would assume is the house. The battery can go most anywhere, closer is better with the IQ Battery 3/10 , due to wireless comms. Less code restrictions on the garage, but then you'll need another spare conduit.
 

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
If you can wait a little bit, Enphase is coming out with a battery with hardwired comms. I don't know when but it is coming.
Thanks. You are right to wait for the 3rd Gen ESS. They have the equipment: system controller 3 & IQ battery & Combiner 5 but don't have the installation details.
 