Good morning experts,
I am designing a Solar Voltaic System with Enphase equipment from my garage to connect my solar input to the 200A Main Service Panel (MSP) which is 25 feet away.
I have a 60A sub panel in the garage fed by an underground 1” conduit and a double pole 70A breaker from the MSP. If I have all my solar panels install near the garage, I would have my Combiner Box there and have the AC disconnect near/next to the MSP.
Since I cannot run another underground conduit between my garage and the MSP because the surface is paved. I would like to use the existing feeder to my garage to connect my solar input from the combiner Box to the MSP via the AC Disconnect. By doing that, I lost my utility supply source to the garage.
As I only need to feed my MSP with 40A (#8 wires) from the solar source (Combiner Box), and in order to maintain/keep the utility supply source to my garage, I would like to replace/downsize the feeder with #8 wires (40A). That means my underground feeder conduit will have input and output 7 #8 wires (reduced one Ground wire ). Also I need to add 4 #18 wires for Consumption CTs , the total conduit fill is still under 40%.
Just wonder whether it is ok per NEC to run the input and output wires in the same conduit? Also it is hard to put all the wires through the 1" underground conduit - the only bend is the two ends where they daylight? I will check with my electrician, just want to make sure it is workable.
I am designing a Solar Voltaic System with Enphase equipment from my garage to connect my solar input to the 200A Main Service Panel (MSP) which is 25 feet away.
I have a 60A sub panel in the garage fed by an underground 1” conduit and a double pole 70A breaker from the MSP. If I have all my solar panels install near the garage, I would have my Combiner Box there and have the AC disconnect near/next to the MSP.
Since I cannot run another underground conduit between my garage and the MSP because the surface is paved. I would like to use the existing feeder to my garage to connect my solar input from the combiner Box to the MSP via the AC Disconnect. By doing that, I lost my utility supply source to the garage.
As I only need to feed my MSP with 40A (#8 wires) from the solar source (Combiner Box), and in order to maintain/keep the utility supply source to my garage, I would like to replace/downsize the feeder with #8 wires (40A). That means my underground feeder conduit will have input and output 7 #8 wires (reduced one Ground wire ). Also I need to add 4 #18 wires for Consumption CTs , the total conduit fill is still under 40%.
Just wonder whether it is ok per NEC to run the input and output wires in the same conduit? Also it is hard to put all the wires through the 1" underground conduit - the only bend is the two ends where they daylight? I will check with my electrician, just want to make sure it is workable.