garyfitzgerald
Member
I am feeding a centrifical chiller motor with (3) 4/0 XHHW conductors. Supply is 3 phase 480v. The conduit thermal scan is 127 degrees F. Ambient temperature is 74 degrees F. Load on the conductors is A=198, B=194 and C=160 amps. The customer (federal government) is concerned about the temperature of the conduit. The conductors read at 116 degrees F. inside the VFD cabinet at the terminations. I know that the load is within the conductor capacity and the temperature is within the insulation capacity. I'm trying to contact Southwire Tech Support to see if they can provide some insight. Is there somewhere else that may provide info on conductor temperature at various loads or do I have a real concern here?