Is there a code that says I have to install a J-box for every hundred feet of pipe? I've done this to engineer specs before but is there a specific code for this? I can't seem to find it anywhere in the book........thanks....
Not for Electrical, but I have seen a similar requirement in communications standards for data wiring.
where do you see that. It could be a enngineer requirement and nothing else.
TIA/EIA-569: ?No section of conduit shall be longer than 30m (100ft) or contain more than two 90 degree bends between pull points or pull boxes."
I believe the section is 4.4.2.1. I've never been on a job that required this to be followed.
Come on over here! We require it.
In addition to this some manufacturers guidelines, such as Superior-Essex, state to follow Table 1 Chapter 9 (40%) with a 15% reduction for every 90% bend.View attachment 3887
Come on over here! We require it.
In addition to this some manufacturers guidelines, such as Superior-Essex, state to follow Table 1 Chapter 9 (40%) with a 15% reduction for every 90% bend.View attachment 3887
I agree where is 'here'?
good electricians do put a pull point every 100' and we all know why. .......