CONDUIT INSULATING BUSHING
VLK
New member
Can you split a bushing which threads on a conduit connector? The installer then screws it onto the connector and super glues the split.
[ October 27, 2005, 09:56 AM: Message edited by: VLK ]
Re: CONDUIT INSULATING BUSHING
I'm sure that you can do anything ya want!
HOWEVER - if you cut a bushing, you destroy it's UL rating.
The NEC requires the use of RATED devices. Once CUT (even if re-glued) You have still altered, the tested, and approved UL rateing. :cool:
1) What is "rated"? I know what "approved", "identified" and "listed" are, but I have never heard of the term "rated".
2) What is your code reference to back up your statement?
300.4(F) does not require the bushing to be listed, so I highly doubt that these fittings are listed. With that said, I know of no code reference to prohibits such practice, although I think a person might be able to stretch 300.18(A) to require this fitting to be installed before the conductors are pulled.
Ryan,
The .6 sections of the raceway articles requires the use of a listed bushing.
Don
Ryan,
The plastic bushing I have in my hand,has UL on it brother.(I had to go check too) :D
*you still remain as my hero, brother Jackson.
:cool:
Here's a solution to the OP's delima.
From Arlington products
ADJUSTABLE THROAT LINERS
To be installed in fittings after conduit, fitting and wire are in place.
Allows installation to meet local electrical code.
Polypropylene.
CATALOG
NUMBER UPC/DCI/NAED
MFG #01 8997 TRADE
SIZE UNIT
PKG STD
PKG DIM
A DIM
B
4001 04001 1/2 25 100 .670 .900
4002 04002 3/4 25 100 .710 1.220
4003 04003 1 25 100 .880 1.450
4004 04004 1-1/4 10 40 1.015 1.735
4005 04005 1-1/2 10 40 1.015 2.050
4006 04006 2 10 40 1.250 2.312
E60812 LR49636
Roger
Roger posted a picture of what I've called an "Ut Oh" bushing. They can be installed after the pull is installed. I havn't forgotten many bushings, but I have destroyed my share in the pull. Sawed through a few PVC ells with the rope too. Arlington needs to make something to fix that problem now.