CONDUIT INSULATING BUSHING

Merry Christmas
Status
Not open for further replies.

VLK

New member
Can you split a bushing which threads on a conduit connector? The installer then screws it onto the connector and super glues the split.

[ October 27, 2005, 09:56 AM: Message edited by: VLK ]
 
Re: CONDUIT INSULATING BUSHING

I'm sure that you can do anything ya want!

HOWEVER - if you cut a bushing, you destroy it's UL rating.

The NEC requires the use of RATED devices. Once CUT (even if re-glued) You have still altered, the tested, and approved UL rateing. :cool:
 
Re: CONDUIT INSULATING BUSHING

Originally posted by electric_instructor:

The NEC requires the use of RATED devices.
1) What is "rated"? I know what "approved", "identified" and "listed" are, but I have never heard of the term "rated".

2) What is your code reference to back up your statement?
 
Re: CONDUIT INSULATING BUSHING

300.4(F) does not require the bushing to be listed, so I highly doubt that these fittings are listed. With that said, I know of no code reference to prohibits such practice, although I think a person might be able to stretch 300.18(A) to require this fitting to be installed before the conductors are pulled.
 
Re: CONDUIT INSULATING BUSHING

Ryan,
The .6 sections of the raceway articles requires the use of a listed bushing.
Don
 
Re: CONDUIT INSULATING BUSHING

Originally posted by ryan_618:
so I highly doubt that these fittings are listed.
Ryan,
The plastic bushing I have in my hand,has UL on it brother.(I had to go check too) :D

*you still remain as my hero, brother Jackson.
:cool:
 
Re: CONDUIT INSULATING BUSHING

Here's a solution to the OP's delima.

From Arlington products

4001_1.gif



ADJUSTABLE THROAT LINERS
To be installed in fittings after conduit, fitting and wire are in place.
Allows installation to meet local electrical code.

Polypropylene.
CATALOG
NUMBER UPC/DCI/NAED
MFG #01 8997 TRADE
SIZE UNIT
PKG STD
PKG DIM
A DIM
B
4001 04001 1/2 25 100 .670 .900
4002 04002 3/4 25 100 .710 1.220
4003 04003 1 25 100 .880 1.450
4004 04004 1-1/4 10 40 1.015 1.735
4005 04005 1-1/2 10 40 1.015 2.050
4006 04006 2 10 40 1.250 2.312


E60812 LR49636

ul_sa.gif


Roger
 
Re: CONDUIT INSULATING BUSHING

Roger posted a picture of what I've called an "Ut Oh" bushing. They can be installed after the pull is installed. I havn't forgotten many bushings, but I have destroyed my share in the pull. Sawed through a few PVC ells with the rope too. Arlington needs to make something to fix that problem now.
 