If the PVC was on the side away from traffic, its protected somewhat. But 1,000 feet will require multiple expansion couplings, and the PVC has to be fastened closer than the NEC allows to prevent sagging. Jersey barriers have wire loops on the ends and use a large pin to couple together (the ones here do)Does the pin go into the ground, or will the jersey barrier defect if hit?
IMO PVC run horizontally on a building always sags and looks like a DIY job. RMC would be faster to install using 1 hole mallable straps and zamac anchors. PVC would have to be held level before fastening, and the PVC straps have to allow for movement for the expansion to go to the coupling
If possible please post back how many expansion couplings are required for 1,000 ft, but perhaps its 1,000 ft barrier with PVC on part of it
Also at 1,000 ft RMC may require an expansion coupling.