Ok, maybe Im just being to strict in 'NEC' code following, but I just got done helping a guy on a job (was done with mine) where the conduit is overfilled. This is 1" emt, it has 15 #10's 4 #12's Thhn insulation. You can double check my math but I come up with too many wires in this pipe. (this why the pull was too hard) and yet it was forced in there anyways. Have any of you run into this where there were too many wires and they just 'force more in there'???
Oh by the way we wont even go into the derating that nots being done, even though i know alot of guys dont derate. Those #12's either should be #10's or on a 15amp breaker. I counted 10 ccc and this is not counting the neutrals (dont know it they have nonlinear loads). I also discovered that the #10's that were pulled are spliced into #12's at another j box down stream just before they get to the deivices (mostly receptacles, light etc). This should be #10's all the way.
I didnt realize this error in his stuff until it was done. The over fill just looked funny to me at first until I double checked my math. I feel Ive been suckered into being a HACK!! What do you think??
Oh by the way we wont even go into the derating that nots being done, even though i know alot of guys dont derate. Those #12's either should be #10's or on a 15amp breaker. I counted 10 ccc and this is not counting the neutrals (dont know it they have nonlinear loads). I also discovered that the #10's that were pulled are spliced into #12's at another j box down stream just before they get to the deivices (mostly receptacles, light etc). This should be #10's all the way.
I didnt realize this error in his stuff until it was done. The over fill just looked funny to me at first until I double checked my math. I feel Ive been suckered into being a HACK!! What do you think??