Is the code specific on the type of conduit that passes through a roof?
M Michaelmechanic Member Location Ft lauderdale fl Lu 728 Sep 10, 2014 #1 Is the code specific on the type of conduit that passes through a roof?
kwired Electron manager Location NE Nebraska Sep 10, 2014 #2 Only that it be suitable for the conditions it is subjected to. So if you passed flexible metal conduit through a roof, chances are above the roof is a wet location, FMC is not for wet locations, so the above roof portion would not be compliant.
Only that it be suitable for the conditions it is subjected to. So if you passed flexible metal conduit through a roof, chances are above the roof is a wet location, FMC is not for wet locations, so the above roof portion would not be compliant.