- Location
- Illinois
- Occupation
- retired electrician
It appears to me that the code does permit a standard coupling between the explosion proof enclosure and its seal.Has been touched already though that you wouldn't have a coupling between an enclosure with ignition hazards and the conduit seal, in fact I believe (going from memory here) that there is limitations on what fittings can be between the enclosure and the seal fitting, and they are mostly limited to explosion proof unions, explosion proof capped elbows and explosion proof flexible couplings.
I would think a standard coupling wouldn't even be desired in most cases over a union type of coupling for assembly reasons.
I know that others see the word "explosionproof" as modifying all of the items, but I don't read it that way. I would never install a standard coupling in that location, but I believe that the code permits it.501.15(A)(1)(1) ... Conduit seals shall be installed within 450 mm (18 in.) from the enclosure. Only explosionproof unions, couplings, reducers, elbows, capped elbows, and conduit bodies similar to L, T, and Cross types that are not larger than the trade size of the conduit shall be permitted between the sealing fitting and the explosionproof enclosure