I am currently doing a new gas station and dispensers. I have the conduit seals in place and the wires pulled. There is one spare conduit into each dispenser. The station will be testing and doing a final to open. In the past, I have, as other contractors have, not poured the conduit seals until all operations were tested and passed. This allowed the electrical contractor to make changes or corrections prior to the final action of pouring the seals. Was there ever an informational note or wording that allowed for this time between operation and testing? I have 2 answers from 2 AHJs. The first is that the seals must be poured prior to any operation. The second answer is, not to pour the seal until all operations have been tested. I fully understand the importance of the conduit seals, many of which have never been poured!

A second question would be how to seal the spare conduit with no wires pulled?

Thank you for your time for those who answer these questions.

BigWyo
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I'm going to answer your second question first. Cap both ends of the spare conduit with a coupling and a plug. Since there's no wiring inside there's not much chance of igniting anything, even with possible ignitable material inside.

The first question is a bit more complicated. If fuel has already been introduced to the dispenser system, the first AHJ is correct - you already have your classified locations and must seal accordingly. If no fuel is present, the second AHJ's answer is OK. However in both cases you must have the area classification documented. [Section 500.4(A)]
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'm going to answer your second question first. Cap both ends of the spare conduit with a coupling and a plug. Since there's no wiring inside there's not much chance of igniting anything, even with possible ignitable material inside.

The first question is a bit more complicated. If fuel has already been introduced to the dispenser system, the first AHJ is correct - you already have your classified locations and must seal accordingly. If no fuel is present, the second AHJ's answer is OK. However in both cases you must have the area classification documented. [Section 500.4(A)]

Bob,
The question of sealing empty conduits seems to come up fairly often for me. Certainly they have to be capped to prevent the passage of gases but the question always seems to center around how. We see typically 2 scenarios. The first is there is a seal off in place. Should we pack and pour the empty seal off? Or can one simply put plug in the open end of the seal off? The issue I see with not pouring the seal off is that you then have 3 threaded joints (each end of the seal plus the side plug) which seems to violate the intent of the code requiring the seal to be the first fitting/joint.
The second scenario is no seal off but simply use a coupling and plug as you indicated. Again there seems to be an issue of violating the first fitting joint rules.
Your thoughts would be appreciated.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Bob,
The question of sealing empty conduits seems to come up fairly often for me. Certainly they have to be capped to prevent the passage of gases but the question always seems to center around how. We see typically 2 scenarios. The first is there is a seal off in place. Should we pack and pour the empty seal off? Or can one simply put plug in the open end of the seal off? The issue I see with not pouring the seal off is that you then have 3 threaded joints (each end of the seal plus the side plug) which seems to violate the intent of the code requiring the seal to be the first fitting/joint.
The second scenario is no seal off but simply use a coupling and plug as you indicated. Again there seems to be an issue of violating the first fitting joint rules.
Your thoughts would be appreciated.
This is a very reasonable question; I'm surprised it hasn't been raised before.

Section 501.15 IN No.2 outlines the main purposes of sealing: (in reverse order) prevent the passage of flames and minimize (not necessarily prevent) the passage of gases and vapors. A careful review of the rest of Section 501.15 reveals there are two primary types of seals: enclosure and boundary.

With respect to the OPs question, I submit the "seal" in question can only be a boundary seal.

Enclosure seals are critically important; they prevent the passage of flames AND there is a clear (and likely) source of ignition.

Boundary seals are considerably less so. There is a modest potential that syphoning or differential pressure could cause gases or vapors to migrate. However, in the OP's scenario, both are nearly impossible whether the source is Division 1 or 2.
 
Location
Wyoming
There is a modest potential that syphoning or differential pressure could cause gases or vapors to migrate. However, in the OP's scenario, both are nearly impossible whether the source is Division 1 or 2.

I have noticed several installations where the seal off devices are inside the building. With warmer temps inside, and colder temps outside, do you believe the siphoning effect would be greater?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Install couplings and plugs with teflon tape on empty capped conduits if your afraid of transmission through it.
Teflon tape or other pipe joint compounds do little to improve the seal on our straight thread couplings. I typically use a plumbers pipe cap for this purpose.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Teflon tape or other pipe joint compounds do little to improve the seal on our straight thread couplings. I typically use a plumbers pipe cap for this purpose.

Yep, in my view a plumbing cap would certainly achieve the desired result for spare raceways. You also get to satisfy the first fitting requirement at the boundary. Effective, cheap and swift. This is what is so frustrating with prescriptive codes as common sense and the code collide.
I would not have an issue in approving a plumbing cap used for this purpose if it was my call. One would think that somebody like Appleton would have submitted a capping product for approval long ago. It just seems so simple but I guess I'm just a simple guy.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Your not using enough Teflon.
While pipe joint compounds do act to fill small imprecations in the threads, their real purpose is to provide lubrication so the joint can be tightened enough to provide a solid metal to metal interference fit to seal the joint.
 
Last edited:

AKElectrician

Senior Member
While pipe joint compounds do act to fill small imprecations in the threads, their real purpose is to provide lubrication so the joint can be tightened enough to provide a solid metal to metal interference fit to seal the joint.

STL (Steel Thread Lube) could be used instead? From my very limited experience of plumbing I find that hard to believe, but I am a electrician not a a plumber so.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I have no problem with either Teflon tape or plumber's caps, primarily because I'm not too concerned about gas/vapor migration in empty conduits in the first place; especially if the "source" is Class I, Division 2 and only slightly more in Division 1.

In "open air" there is virtually no greater possibility for gas/vapor migration through the empty conduit than random migration outside of it.

Where the boundary is a physical barrier, such as a wall or grade, it takes a significant pressure differential for an empty conduit to be a concern and virtually any method of capping both ends will be suitable.
 

AKElectrician

Senior Member
I have no problem with either Teflon tape or plumber's caps, primarily because I'm not too concerned about gas/vapor migration in empty conduits in the first place; especially if the "source" is Class I, Division 2 and only slightly more in Division 1.

In "open air" there is virtually no greater possibility for gas/vapor migration through the empty conduit than random migration outside of it.

Where the boundary is a physical barrier, such as a wall or grade, it takes a significant pressure differential for an empty conduit to be a concern and virtually any method of capping both ends will be suitable.

Agree 100%.
 