I am going to agree just because it is my new years resolution to agree with everyone. This is painful. The new warm and fuzzy cow.
I am going to agree just because it is my new years resolution to agree with everyone. This is painful. The new warm and fuzzy cow.
That would be notes 5 and 9 to Chapter9, Table 1.Au contraire. Notes 5 and 9 to Table 9.
That is so moooooving!I am going to agree just because it is my new years resolution to agree with everyone. This is painful. The new warm and fuzzy cow.
keep in mind different jackets need more space do to what type it maybe do to drag and type of outer coating some do not pull very good some do . comments ?
So the NEC allows us to pull NM cables and things like this in conduit?
Yes, if you're a glutton for punishment.So the NEC allows us to pull NM cables and things like this in conduit?
If I can run NM in an insulated wall why would anyone think that running it in conduit would be a heat problem? A metal conduit could actually work like a heat sink pulling heat from the cable and radiating that heat to the environment over it's increased surface area.
do you say that because a lot of inspectors will try to fail you for that?Yes, if you're a glutton for punishment.
No, because it's hard to do. Some time back, I posted a chart with cross sectional areas of romex. I'm not sure if I correlated that to the minimum conduit size in that chart or not.do you say that because a lot of inspectors will try to fail you for that?
OK, OK, OK. That's the last time I have the Reader's Digest Condensed Books editorial staff spot-check my posts.That would be notes 5 and 9 to Chapter9, Table 1.
IMO the bending radius does not change the pulling force required assuming the radius was not below minimum to start with.
The only thing a larger radius sweep does is lower the sidewall pressure on the cable.
Wouldn't that pressure translate into friction? And more force needed to overcome that friction?
Seems it's always harder to pull through 200' of pipe when theres's 2 or 3 90s in it as opposed to the exact same length but a straight shot.