dlhoule said:It is also a common sense thing.
It's also a common sense thing.
A visit from the grammer police ?
:twisted:
dlhoule said:It is also a common sense thing.
It's also a common sense thing.
iwire said:dlhoule said:It is also a common sense thing.
It's also a common sense thing.
I disagree it is a 'code' thing. :lol:
The code does not allow EMT running through drywall to be supported by the 'hole'.
If you do so (and I have) and the inspector decides to enforce the code as written you will not have a leg to stand on regardless of how well the EMT may be supported by the 'hole'.
Jim W in Tampa said:iwire said:dlhoule said:It is also a common sense thing.
It's also a common sense thing.
I disagree it is a 'code' thing. :lol:
The code does not allow EMT running through drywall to be supported by the 'hole'.
If you do so (and I have) and the inspector decides to enforce the code as written you will not have a leg to stand on regardless of how well the EMT may be supported by the 'hole'.
Code number Bob ?
338.30(B) Supports. Horizontal runs of EMT supported by openings through framing members at intervals not greater than 3 m (10 ft) and securely fastened within 900 mm (3 ft) of termination points shall be permitted.
celtic said:dlhoule said:It is also a common sense thing.
It's also a common sense thing.
A visit from the grammer police ?
:twisted:
Jim W in Tampa said:celtic said:dlhoule said:It is also a common sense thing.
It's also a common sense thing.
A visit from the grammer police ?
:twisted:
It's fixed and i paid the fine :lol:
celtic said:I would think the words we are looking for are:
securely fastened in place and supported 358.30
Resting in a hole does not meet that requirement.
Jim W in Tampa said:.NEC did not define framing so its left to the dictionary.
Jim W in Tampa said:Sounds to me that everything making the wall is FRAMING
Jim W in Tampa said:Without NEC giving a definition just what would you care to use ?
NEC really needs to print a dictionary for every word it uses.Without a clear definition we end up with this kind of problem often.
Jim W in Tampa said:Without NEC giving a definition just what would you care to use ?
Jim W in Tampa said:Is grid wire a framing member ?Seen plenty of emt hung from them with batwings
tonyi said:OK, now lets make this "interesting"...
Is a hole through Durock a framing member? I contend Durock just a very skinny concrete wall :lol:
Jim W in Tampa said:Back to resultsMain Entry: 2neutral
Function: adjective
celtic said:dlhoule said:It is also a common sense thing.
It's also a common sense thing.
A visit from the grammer police ?
:twisted:
sandsnow said:celtic said:dlhoule said:It is also a common sense thing.
It's also a common sense thing.
A visit from the grammer police ?
:twisted:
A visit from the grammer police ?
A visit from the grammar police ?
Courtesy your local spelling police :twisted:![]()