Conduit Support Wire

Merry Christmas
Status
Not open for further replies.

kvoll

New member
Location
California
If construction is based on the 1996 NEC can conduits and boxes be supported by using a # 12 wire suspended from the roof structure without being secured on the bottom?
In a T-bar ceiling conditions these support wires are independent from the T-bar grid system. Are these support wires required to be secured to the the grid on the bottom side?
 
Re: Conduit Support Wire

Not sure about the 96 (don't have it handy ) but in 99 the requirement that the support wire be secured at both ends is Article 300 Wiring Methods----300-11 (a) Securing and Supporting
 