Conduit support

Status
Not open for further replies.

newt

Senior Member
Looking for section of the code ---?????

To verify that using pvc straps to support emt is a code violation. Thanks!
 
For instance

Pipe%20Hangers.jpg
 
352.6 Listing Requirements.
RNC, factory elboxw, and associated fittings shall be listed.

344.6 Listing Requirements.
RMC, factory elboxw, and associated fittings shall be listed.


As Bob posted, you may find some fittings listed for one another.
 
Thanks. Is it a violation to use steel straps on pvc because it does not allow for movement of pipe?
 
352.6 Listing Requirements.
RNC, factory elboxw, and associated fittings shall be listed.

344.6 Listing Requirements.
RMC, factory elboxw, and associated fittings shall be listed.

IMO those sections do not apply to supports, ..... or strut clips are in violation.:smile: Of course the AHJ still has to approve them.
 
Looking for section of the code ---?????

To verify that using pvc straps to support emt is a code violation. Thanks!

The fittings do have to provide a means for expansion and contraction due to temperature.
See 352.30. ...and shall be fastened so that movement from thermal expansion or contraction is permitted.

I believe using PVC straps on EMT is going to allow for expansion and contraction, the other way round may be a problem.
 
352.6 Listing Requirements.
RNC, factory elboxw, and associated fittings shall be listed.

344.6 Listing Requirements.
RMC, factory elboxw, and associated fittings shall be listed.


As Bob posted, you may find some fittings listed for one another.
Pierre,
Panel 8 says that support straps are not fittings.
8-5 Log #2239 NEC-P08 Final Action: Reject
(342.6 Exception (New) )
________________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise as follows:
342.6 Listing Requirements. IMC, factory elbows, and couplings, and
associated fittings shall be listed.
Exception: Raceway support fittings and accessories shall not be required to
be listed .
Substantiation: The Article 100 definition of ?fitting? seems to include
raceway supports. Many of the commonly used raceway support straps,
clamps, and other items are not listed.
Panel Meeting Action: Reject
Panel Statement: Conduit support accessories are not considered ?Fittings?.
Sections 300.6 and 300.6(A) require support hardware to be constructed of
materials suitable for the environment for which they are to be installed.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
 
Status
Not open for further replies.
Top