220/221 said:
I am CERTAIN that the NEC allows (or doesn't prohibit) sleeving NM in conduit outdoors. It is done on every single residential rooftop AC unit . . .
Not the compliant ones.
220/221 said:
Code section for a definition of "sleeve"?
Yes, NM may be sleeved, but only where the NM would otherwise be allowed. Sleeving does not change the "location."
220/221 said:
Have you ever wired a resi rooftop AC?
Does your house have a rooftop AC?
Did you ever question it's compliance?
I still can't believe that it's a violation.
Yes, no, N/A, and 'believe it.'
220/221 said:
The next question is "why is it done every single day?"
You'd have to ask the inspectors who are allowing it.
220/221 said:
Eh...I'm goin with, the inside of the conduit is normally dry.
Not if it's outdoors. Keep in mind that the interior of conduit is not a location; the environment of the conduit is.
acrwc10 said:
Alot of people don't wash thier hands after using the restroom either, dosn't mean they shouldn't , maybe its easier and quicker, But its still not healthy.
I don't know about you, but when I'm working, I wash my hands
before using the facilities.
220/221 said:
1) What is a "multi wire conductor" as referred to in 225.10 in the 2005 NEC?
2) How would you install the circuit to a residential rooftop AC?
1) It's "multi-conductor cable", and it's a cable that contains more than one conductor. However, that does not mean that every multi-conductor cable made may be used outdoors.
2) I use a water-tight raceway with individual conductors that are wet-use-rated, meaning a W in the type.
1) why is it allowed in literally milions of applications and
2) How do YOU do it?
1) It may be
used in millions of apps, but that doesn't make it
lega to do.
One more time.You have you NM running thru the attic and at some point it has to exit thru the roof and go to the AC unit. How do you get it there?
If your home run is NM, you must transition to another wiring method before passing through the building envelope.
The other option is to use an exterior-compliant wiring method for the entire branch circuit.
220/221 said:
I'd not only ALLOW NM to be protected in emt I would require ANY cable to be protected unless it was in the wall/attic. It cracks me up that cable can be strung outside a house but protecting NM with emt is considered unsafe.
Again, it is permissible to protect cables with conduit, but that does not change the permitted location of each cable type. For example, NM can be sleeved indoors and UF can be sleeved outdoors.