M maylo1st Member Location Pennsylvania Apr 15, 2003 #1 where does it say that conduit must be round or circular or somthing to that affect in the code book?
where does it say that conduit must be round or circular or somthing to that affect in the code book?
iwire Moderator Staff member Location Massachusetts Apr 15, 2003 #2 Re: conduit In the 2002 NEC it would be section 24 of the raceway articles. XXX.24 Bends - How Made "...the internal diameter of the conduit will not be effectively reduced..."
Re: conduit In the 2002 NEC it would be section 24 of the raceway articles. XXX.24 Bends - How Made "...the internal diameter of the conduit will not be effectively reduced..."
S sparkmantoo Member Location Virginia Apr 15, 2003 #3 Re: conduit surface metal raceways like the thin wiremold, is not circular but it can be bent. i have done it with believe it or not with a wiremold bender. its almost like a 3/8 trade size. no b.s.
Re: conduit surface metal raceways like the thin wiremold, is not circular but it can be bent. i have done it with believe it or not with a wiremold bender. its almost like a 3/8 trade size. no b.s.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 15, 2003 #4 Re: conduit Look at the xxx.2 section of each of the conduit articles. They all say "raceway of circular cross section", or something similar. Don
Re: conduit Look at the xxx.2 section of each of the conduit articles. They all say "raceway of circular cross section", or something similar. Don