I have the following situation. 600 mcm main service conductors run from the utility transformer to 3 main distribution panels through 4? rigid nonmetallic conduits. The problem is that where the conductors exit the conduits there is no bushing installed. Of course, this is in violation of 300-4(f) which requires such bushings. However, the installation is nearly complete and it would require significant effort to rectify. Inasmuch as the conductors appear unharmed (I plan to check insulation integrity with a Megger), would a ?retrofit? using a split bushing, not necessarily Listed for the purpose, or perhaps even a wide ?Ty-wrap? around the conductors where they emerge from the conduit, be acceptable to keep the conductors away from the edges of the conduit, and still be deemed to be in compliance of the NEC?
Given the size of the conductors, the installation is pretty rigid and they will not move to be abraded by the conduit?s edge.
Any other suggestions?
Appreciate your help.
Thanx.
Heinz R.