Conduits Exposed to Sun Light

faresos

Senior Member
Do I still need to derate the feeder conductors if the conduits are installed on an outdoor pipe rack above ground and exposed to sun light? The NEC code (310.15.B.2) only mentions that derating is required if installed above the roof. Any thoughts? Thanks,
 
By Code I think to the ANSI temperature for that area.
Which seemingly no one understands. :unsure: This is another poorly written code section. Can't we just get a table that states what the derating is based on temperature at a given location?
 
Thank you all for the responses. That was my concern as to what temperature to use since it will be in metal conduit and will get hot, as others indicated.
 
does painting the conduit with solar reflective white paint helps a lot with reducing the heat inside the conduits? Other option might be the use of cable tray with cover on a pipe rack (20ft above ground), might be an option as well. Is there specific recommended cable tray to be used with this option? it's about 50ft run
 
I don't think that code actually specifies the temperature you need to consider for the situation you describe. Code says you are required to derate for ambient temperature, but doesn't really tell you what temperature to use.

The conduit will be in pretty unobstructed air flow so that will help, but sun can heat stuff up quite a bit. You might consider a simple sunshade spaced a couple of inches above the conduit.
 
Table 310.16 is based on 3 current-carrying conductors in a 78°F to 86°F ambient temperature.

Ambient Temperature
69 to 770F
Ambient Temperature
78 to 860F (30°C)
Ambient Temperature
87 to 95°F
90°C Table Ampacity
Correction Factor =
104% (1.04)
90°C Table Ampacity
Correction Factor =
100% (1.00)
90°C Table Ampacity
Correction Factor =
96% (0.96)
 
does painting the conduit with solar reflective white paint helps a lot with reducing the heat inside the conduits? Other option might be the use of cable tray with cover on a pipe rack (20ft above ground), might be an option as well. Is there specific recommended cable tray to be used with this option? it's about 50ft run
Shade works really really well. A little sun hat made of sheet metal works awesome.
Conduit being galvanized is hard to paint in a way that will work reliably over the long term.... and you can be sure even if you paint it, nobody else ever will.
 
Not one of the things I worry about. There must be a million miles of conduit installed on rooftops pre-temp derating and it's standing the test of time.
I don't think i have ever derated for temperature. "We" have this unspoken agreement that i wont increase the ampacity of my underground conductors dur to cool temps, and i wont decrease for high temps like in attics and such.
 
From 310.15(B)(2)

Informational Note:
The ASHRAE Handbook — Fundamentals is one source for the ambient temperatures in various locations.


ETA: The ASHRAE site is hard to navigate and find the information, at least for me it is.


However, Copper Development has the same info. Although it mentions roof top, but it does give you an idea what the average highest temperature is to use for your cals.

 
Conduit being galvanized is hard to paint in a way that will work reliably over the long term.... and you can be sure even if you paint it, nobody else ever will.
When I was a kid we use to etch galvanized with vinager before we painted. The household stuff helped but if you wanted it to last you needed something high concentration like this
Screenshot 2025-10-15 123521.png
There are also self etching primers , but the whole thing is a lot more work, and yeah it's never going to be done again
 