Conduits Going from unclassified to classified area

Status
Not open for further replies.
Hello All,
Can someone please help me find what the NEC code says about sealing the penetration hole when a conduit is run from a unclassified to a classified class 1 div 1/2 location. I am already aware of 501.15 which talks about the seals in the conduit and cable. But what about the details regarding sealing the penetration hole?

Thank you, have a great day!
 
Not all hazardous location "boundaries" occur at a wall, floor or other physical barrier. Penetrations in such barriers are not covered by the NEC, but very well may be by other codes.
 