Well there is no electrical formula its set by the structual engineer in your specs for the last  35 years of construction most PT decks you must space 2 inches apart conduits and your largest conduit in a slab is  min 2 inches  from top 2 inches from bottom covered .
Just a example  1 inch  to 1 1/4 inch is the largest conduit but ask you engineer in a RFI.
You must use chairs you can run across but not paralleled to pt cables meaning touching them .
There is a set distance on most jobs by structual engineer  and just for  forum info you will never see pt cable in a ground floor ever only elevated decks .
You can cross them you can lay on them but  stay away from columns where there combined .
If you install sleeves for riser conduits do not install touching pt cables they will pop your sleeve out when stressed but tensioning .
When they tighten up the cables its 5000 lbs of pull so if your on top of pt its bad news use chairs save your conduit .
And never  hit one with a core drill !  I have 