condulet bodies

Status
Not open for further replies.
Yes as long as the conduit body has it's cu in capacity marked on it. 314.16(C)(2).
 
314.16(C)(2): With Splices, Taps, or Devices. Only those conduit bodies that are durably and legibly marked by the manufacturer with their volume shall be permitted to contain splices, taps, or devices. The maximum number of conductors shall be calculated in accordance with 314.16(B). Conduit bodies shall be supported in a rigid and secure manner.
 