240.21(C) states "set of conductors .... shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6)." What does the "at the secondary" mean?
If I ran 20' of secondary conductors to a panelboard with 200A MCB, and the 200A MCB meets the requirement of 450.3 (transformer secondary protection), then, isn't the overcurrent protection by the 200A OCPD located "at the secondary?"
From the way I understand, 240.21(C) allows me not to have the secondary OCPD, but then at least 240.21(C)(3)~(6) says, the secondary conductor shall terminate to a single CB (or one set of fuses). Isn't the single CB considered to be secondary OCPD? I thought 240.21(C) rules allowed me not to have secondary OCPD.
If I ran 20' of secondary conductors to a panelboard with 200A MCB, and the 200A MCB meets the requirement of 450.3 (transformer secondary protection), then, isn't the overcurrent protection by the 200A OCPD located "at the secondary?"
From the way I understand, 240.21(C) allows me not to have the secondary OCPD, but then at least 240.21(C)(3)~(6) says, the secondary conductor shall terminate to a single CB (or one set of fuses). Isn't the single CB considered to be secondary OCPD? I thought 240.21(C) rules allowed me not to have secondary OCPD.