First time posting - I am an electrician on a college campus and had a problem: one of the maintenance workers turned off a 20 amp single pole breaker in a 100 amp 3 phase 277-480 sub panel feeding a 277 volt lighting circuit to replace a bad ballast. Once the ballast was replaced they turned the breaker back on not realizing the wire nut was not tight enough and came loose and instead of tripping the 20 amp breaker or the 100 amp main in the sub panel, it tripped the 1600 amp main feed to the building. Killed all the lights in the building! Some students were happy! Lol
My question is why did it trip the main?
My question is why did it trip the main?