The change order was accepted to put a non fused disconnect between the load center and the source. A de-energized panel is a happy panel. We can work in it safely without cat 4 gear the whole time now. Thanks for the input.
Non-fused disconnects are often not the ideal item for disconnecting 'sources' as UL typically limits them to 10kA short circuit current, unless there is an proper upstream protective device.