- Occupation
- Licensed Electrician
I'm eliminating EGCs from the discussion for a second since they only exist for a fault clearing path.
So you have two hots from the utility on one side of the transfer switch and two hots from the generator on the other side of the transfer switch. You have one neutral from the utility and one neutral from the generator landing on a common buss in the transfer switch. Electrons are only flowing from the generator to the load and back to the generator source neutral or they are flowing from the utility to the load and back on the utility source neutral. There is never any parallel neutral current on any neutral wires if everything is wired properly.
Unlessss you have a second neutral bond somewhere in the system. Then you could possibly have some neutral current flowing on some metal parts trying to get to its respective source.
So you have two hots from the utility on one side of the transfer switch and two hots from the generator on the other side of the transfer switch. You have one neutral from the utility and one neutral from the generator landing on a common buss in the transfer switch. Electrons are only flowing from the generator to the load and back to the generator source neutral or they are flowing from the utility to the load and back on the utility source neutral. There is never any parallel neutral current on any neutral wires if everything is wired properly.
Unlessss you have a second neutral bond somewhere in the system. Then you could possibly have some neutral current flowing on some metal parts trying to get to its respective source.