I am designing a chart to simplify feeder calculations. So far, I have come up with something like this:
1000amp load
1000 amp breaker
(2) sets of 3 900kcm hots and (2) sets of 500kcm neutral
OR
(3) sets of 400kcm and 4/0
OR
(4) sets of 4/0 and 3/0 "neutral"
OR
(5) sets of 3/0 @200amps and 2/0 grounded conductor.
But I cannot make head nor tail of 250-122(f)(1) which says 'base on Table 250-122' and then (a) says it doesn't need to be larger than the circuit conductor. Also, there is something about at least 12 1/2% of area of hots if they are [added together] more than 1100kcmil.
So what is the secret, Excel digestible, formula for the green ["equipment gtounding conductor"]?
~Peter