I was reading an old post in which the discussion was about an arc flash analysis for a circuit below 240V
According to 130.3 Exception No. 1, an AF hazard analysis is not required if the circuit is <240V and fed by a single xfrmr <125kVA
But that doesn't mean there isn't still a flash hazard, does it? I read that as: there is no detailed analysis required, but you then must use Table 130.7(C)(9) and use the category/PPE per task.
(I realize I just asked this question a few weeks ago, but after reading an old post, people were saying that since there is no analysis required, there is no hazard and no PPE is required. I felt that to be incorrect and I hope no one reads that post and uses the information incorrectly.)
My second question is regarding 130.3(C):
If you have a 120V lighting panel that meets the requirements of 130.3 Ex. 1 (i.e., <240V and fed from a single 125kVA), you are not required to complete an analysis. If you can use Table 130.7(C)(9), as applicable per task, how can you label the panel with a specific label (IE or PPE) if it changes according to task?
Thanks
According to 130.3 Exception No. 1, an AF hazard analysis is not required if the circuit is <240V and fed by a single xfrmr <125kVA
But that doesn't mean there isn't still a flash hazard, does it? I read that as: there is no detailed analysis required, but you then must use Table 130.7(C)(9) and use the category/PPE per task.
(I realize I just asked this question a few weeks ago, but after reading an old post, people were saying that since there is no analysis required, there is no hazard and no PPE is required. I felt that to be incorrect and I hope no one reads that post and uses the information incorrectly.)
My second question is regarding 130.3(C):
If you have a 120V lighting panel that meets the requirements of 130.3 Ex. 1 (i.e., <240V and fed from a single 125kVA), you are not required to complete an analysis. If you can use Table 130.7(C)(9), as applicable per task, how can you label the panel with a specific label (IE or PPE) if it changes according to task?